OpenWay Riva 500W ERT Module Events
Event code |
Event name |
Event description |
---|---|---|
1 |
Inter digit |
There is a corrupt digit in the encoded register reading. |
2 |
Register error |
No communication with register. Note: For the Intelis Gas meter, this corresponds to the "Loss of Meter Communication" tamper bit in Mobile mode which could indicate the index has been removed from the meter. |
3 |
Invalid read |
Register is not sending a valid read. |
6 |
Low battery |
The ERT has a low battery warning. 10% of battery life remains. |
7 |
Consumer leak detected |
The ERT has detected continuous flow over a set period of time. |
8 |
Consumer leak end |
The ERT has detected the end of continuous flow after having reported a leak. |
9 |
Reverse flow detected |
The ERT has detected reverse flow. Note: This is sometimes referred to as backflow. |
10 |
Reverse flow end |
The ERT has detected the end of reverse flow after having reported reverse flow. Note: This is sometimes referred to as backflow. |
11 |
Leak sensor OK |
The ERT detects a leak sensor attached and it is working properly (triggered when the state was previously unknown or previously not working properly). |
12 |
Leak sensor no comm |
The ERT detects a leak sensor is attached, but it is not working properly. |
13 |
Leak sensor detached |
The ERT does not detect that a leak sensor is attached after previously having one attached. |
14 |
Valve OK |
The ERT detects that a remote disconnect valve is attached and it is working properly (triggered when state was previously unknown or previously not working properly). Note: An OW-GRD endpoint sends this event when it detects valve communication after a "Valve No Comms" event. This is similar to a "Cut Cable End" event when communicating with the valve. |
15 |
Valve No Comms |
The ERT detects a remote disconnect valve is attached but it is not working properly. Note: An OW-GRD endpoint sends this event when it detects no valve communication. This is similar to a "Cut Cable Detected" event, but is more explicit for the valve. |
17 |
Pulse mismatch |
The ERT has detected an internal pulse mismatch. |
18 |
Cut cable (pulser) detected |
A physical cut cable has been detected by the ERT.Note: OW-GRD records this event when it detects no valve communication. This is similar to a "Cut Cable Detected" event, but is more explicit for the valve. |
19 |
Cut cable (pulser) end |
A physical cut cable is no longer detected by the ERT.Note: Valid for 500W pulser and 500G remote. OW-GRD uses event 15 for this event. |
20 |
High flow detected |
The ERT detects consumption has exceeded the high flow threshold. |
21 |
High flow end |
The ERT detects consumption has dropped below the high flow threshold after having been in a high flow state. Note: If the device is in a high flow detected state and high flow detection is disabled then this event should be logged immediately. |
500 |
Critical error (internal) |
A critical internal error not described by other events. |
501 |
Right sizing started |
The client has requested a right sizing operation in ERT. |
502 |
Right sizing completed |
The right sizing operation is complete. |
503 |
Right sizing cancelled |
The right sizing operation was cancelled. |
504 |
Flash error |
A flash error has been detected. |
505 |
Meter quiet mode exit |
Occurs when the ERT gets pulses or detects consumption for the first time. |
506 |
Entering OW Riva network mode |
The device has been changed to OpenWay Riva network mode. |
507 |
Set battery params |
Any change to the BatteryUseParameters structure results in this event. |
508 |
Set meter right sizing params |
Meter right sizing parameters have been changed. |
509 |
Key update |
The key has been updated in the device. |
510 |
Device not communicating |
The application has not received any incoming data which indicates that the device may not be communicating on the network. |
511 |
Load profile cleared |
The load profile object has been cleared. |
512 |
Manual time sync |
The time has been changed manually. |
514 |
Legally relevant event log nearly full |
This event occurs when the Legally Relevant log is at 90% of its total capacity. |
515 |
Time sync - over threshold detected |
A time change greater than the warning level threshold has been detected. |
516 |
Time sync - over threshold end |
A time change greater than the warning level threshold has ended and is back below the threshold. |
517 |
Entering 100S mode |
The device has been changed from OpenWay Riva network mode to 100S mode. |
1000 |
Register removal |
Badger extended alarm: bit 0 = register removal. |
1001 |
Meter temperature alarm |
Badger extended alarm: bit 1 = temperature alarm. |
1002 |
End of meter life |
Badger extended alarm: bit 2 = end of life alarm. |
1003 |
Zero consumption detected |
Badger extended alarm: bit 3 = no usage alarm. |
1004 |
Reverse flow meter |
Badger extended alarm: bit 4 = reverse flow alarm. |
1005 |
Leak meter alarm |
Badger extended alarm: bit 5 = leak alarm. |
1006 |
Encoder programming |
Badger extended alarm: bit 6 = program alarm. |
1007 |
Meter tamper |
Badger extended alarm: bit 7 = tamper. |
1500 |
Active reverse flow meter |
Kamstrup extended alarm Byte1: bit 0 = active reverse flow. Debounce every 24 hours. |
1501 |
Historic reverse flow meter |
Kamstrup extended alarm Byte1: bit 1 = historic reverse. The active info-code within the last 30 days, no matter how long the info-code was active. Debounce every 30 days. |
1502 |
Active empty pipe |
Kamstrup extended alarm Byte1: bit 2 = active dry. The meter is in a current empty pipe state. Debounce every 24 hours. |
1503 |
Historic empty pipe |
Kamstrup extended alarm Byte1: bit 3 = historic dry. The active info-code within the last 30 days, no matter how long the info-code was active. Debounce every 30 days. |
1504 |
Active burst |
Kamstrup extended alarm Byte1: bit 4 = active burst. The meter is currently in a high flow state outside of the meter parameters. Debounce every 24 hours. |
1505 |
Historic burst |
Kamstrup extended alarm Byte1: bit 5 = historic burst. Active info-code within the last 30 days, no matter how long the info-code was active. Debounce every 30 days. |
1506 |
Encoder programming |
Kamstrup extended alarm Byte1: bit 6 = encoder setup has been changed one or more times since production. |
1507 |
Active leak meter alarm |
Kamstrup extended alarm Byte1: bit 7 = the meter is in an active leak state. Debounce every 24 hours. |
1508 |
Historic leak meter alarm |
Kamstrup extended alarm Byte1: bit 8 = historic leak. The active info-code within the last 30 days, no matter how long the info-code was active. Debounce every 30 days. |
1509 |
Low temperature alarm |
Kamstrup extended alarm: The minimum meter temperature detected. This alarm is sent when the temperature on the Kamstrup meter is < 36° F. |
1510 |
High temperature alarm |
Kamstrup extended alarm: The maximum meter temperature has been detected. This alarm is sent when the temperature on the Kamstrup meter is > 125° F. |
1513 |
Zero consumption detected |
Kamstrup extended alarm: The meter has detected no usage. |
1600 |
Backflow detected |
Sensus Intelis Water Meter extended alarm: The meter's backflow consumption register indicates a total backflow that is outside of the threshold values for expected backflow. |
1601 |
Empty pipe alarm detected |
Sensus Intelis Water Meter extended alarm: The device detects that the pipe is empty, possibly due to the meter being removed from the installation. |
1602 |
Meter reversed |
Sensus Intelis Water Meter extended alarm: The meter has detected that it has been installed in a reverse orientation. |
1603 |
Battery low |
Sensus Intelis Water Meter extended alarm: The meter's battery life has less than six months (for the NAM meter) or 12 months (for the international meter) remaining. |
1604 |
Leakage |
Sensus Intelis Water Meter extended alarm: The meter has detected a leak. The average flow rate during each of the hours over the past day (for NAM meter) or over a configured number of days (for international meter)was above the leakage flow rate threshold. This event clears when the average flow rate for one hour returns to within the configured threshold. |
1605 |
Burst flow alarm detected |
Sensus Intelis Water Meter extended alarm: The meter has detected a burst flow alarm which can indicate a broken pipe. |
1607 |
Tamper alarm |
Sensus Intelis Water Meter extended alarm: The meter has detected that the cover was opened. This can indicate that the meter has been tampered with. |
1608 |
Temperature alarm detected |
Sensus Intelis Water Meter extended alarm: The meter has detected a temperature alarm. The meter has reached a temperature that is outside of the temperature range. This event clears after the alarm duration time passes (one day minimum). |
3000 |
Device reconfigured |
The OpenWay Operations Center (OWCM) configuration in the device has changed. |
3001 |
Event log cleared |
The Itron event log has been reset. |
3003 |
Configuration downloaded |
A new configuration has been downloaded. |
3004 |
System reboot |
A watchdog error. Reboot. |
3005 |
System restart |
A planned restart of ERT (for example, after firmware download). |
3006 |
Improper installation detected |
The ERT could not adopt configuration information. |
3007 |
Disconnect completed |
The disconnect command was received and has completed. |
3008 |
Disconnect failed |
The disconnect command was received but failed to execute. The event detail will contain the verbose_result attribute of the DisconnectControl object. |
3011 |
Connect completed |
The reconnect command was received and has completed. Event detail will contain the verbose_result attribute of the DisconnectControl object. |
3012 |
Connect failed |
The reconnect command was received but failed to execute. Event detail will contain the verbose_result attribute of the DisconnectControl object. |
3013 |
Flow restriction setting changed |
A restrict/service limit event was received and has been completed. The event detail will contain the verbose-result attribute of the DisconnectControl object. |
3014 |
Flow restriction setting failed |
A restrict/service limit was received but failed to execute. The event detail will contain the verbose-result attribute of the DisconnectControl object. |
3015 |
Authentication failed |
An application level security failure - authentication. This event occurs with an application level security failure for authentication. |
3016 |
Access control failed |
An application level security failure - access control. This event occurs with an application level security failure for access control. |
3017 |
Key rollover |
A key rollover command received. |
3018 |
Key signing |
An application level security failure - certificate. |
3019 |
Takeover package accepted |
A takeover package was presented and accepted by the ERT. |
3020 |
Takeover package rejected |
A takeover package was presented, but rejected by the ERT. |
3021 |
Replay attack detected |
An application level security failure - replay. |
3022 |
RMA signed authorization received |
A signed authorization with issued-to "Itron-RMA" has been received. |
10000 |
PCOMP changed |
Metrology parameter (PCOMP) changed. |
10001 |
Count rate changed |
Metrology parameter (Count Rate) changed. |
10002 |
Rollover count changed |
Metrology parameter (Rollover Count) changed. |
10003 |
Count sample debounce changed |
Metrology parameter (Count Sample Configuration - debounce parameters) changed. |
10004 |
Encoder driver type changed |
Metrology parameter (Encoder Driver Type) changed. |
10005 |
Prescaler changed |
Metrology parameter (Prescaler) changed. |
10006 |
Initial index |
Metrology parameter (Initial Index) changed. |
10007 |
Image transfer initiated (enabled) |
An image transfer command was initiated. |
10008 |
Image transfer canceled (disabled) |
An image transfer command was canceled. |
10009 |
Image transfer cancel failed |
An image transfer command was canceled but was not successful. |
10010 |
Image verification initiated |
The process to verify an image has begun. |
10011 |
Image verification successful |
The image verification process was successful. |
10012 |
Image verification failed |
The image verification process was initiated, but was not successful. |
10013 |
Image activation initiated |
The image activation process was initiated. |
10014 |
Image activation successful |
The image activation process was successful. |
10015 |
Image activation failed |
The image activation process was initiated, but was not successful. |
10019 |
Load profile interval changed |
A change has been made to the CompressedLoadProfile object capture_period. |
10020 |
Count sample width changed |
Metrology parameter (Count Sample Configuration - sample width parameters) changed. |
10021 |
Count sample rate changed |
Metrology parameter (Count Sample Configuration = sample rate parameters) changed. |